A \( 15 \mathrm{~kW}, 400 \mathrm{~V}, 50 \mathrm{~Hz}, 4 \) poles, three phase delta connected squirrel cage induction motor operates with efficiency of \( 88 \% \) and p.f. of 0.8 . If the machine operates for continuous duty, determine: (i) Starting current if a star/delta starter is used to start the motor (assume starting factor for D.O.L. starter to be 5). (ii) The full load torque, when the motor operates with a slip of \( 4 \% \) (iii) Size of switching devices (iv) Size of cables/wires (v) Size protective devices

Ask by Cole Griffin. in Tanzania
Mar 11,2025

Upstudy AI Solution

Tutor-Verified Answer

Answer

Starting current with star/delta starter: approximately 27.39 A Full load torque: about 95.49 Nm Full load current: approximately 27.39 A Size of switching devices: rated for at least 27.39 A Size of cables: rated for at least 27.39 A Size of protective devices: rated for at least 27.39 A

Solution

To solve the problem step by step, we will extract the known conditions and then calculate each part accordingly. ### Known Conditions: - Motor Power (\( P \)) = \( 15 \, \text{kW} \) - Voltage (\( V \)) = \( 400 \, \text{V} \) - Frequency (\( f \)) = \( 50 \, \text{Hz} \) - Number of Poles (\( P \)) = \( 4 \) - Efficiency (\( \eta \)) = \( 88\% = 0.88 \) - Power Factor (\( \text{p.f.} \)) = \( 0.8 \) - Slip (\( s \)) = \( 4\% = 0.04 \) - Starting factor for D.O.L. starter = \( 5 \) ### (i) Starting Current with Star/Delta Starter The starting current for a D.O.L. starter is given by: \[ I_{DOL} = \frac{P}{\sqrt{3} \cdot V \cdot \text{p.f.}} \] The starting current for a star/delta starter is: \[ I_{star/delta} = \frac{I_{DOL}}{3} \] Let's calculate \( I_{DOL} \) first. ### (ii) Full Load Torque The full load torque (\( T \)) can be calculated using the formula: \[ T = \frac{P \cdot 60}{2 \pi N} \] Where \( N \) is the synchronous speed given by: \[ N = \frac{120 \cdot f}{P} \] ### (iii) Size of Switching Devices The size of switching devices can be determined based on the starting current and the full load current. ### (iv) Size of Cables/Wires The size of cables can be determined based on the full load current and the length of the cable run. ### (v) Size of Protective Devices The size of protective devices can be determined based on the full load current and the starting current. Now, let's perform the calculations for parts (i) and (ii) first. #### Step 1: Calculate \( I_{DOL} \) \[ I_{DOL} = \frac{P}{\sqrt{3} \cdot V \cdot \text{p.f.}} = \frac{15000}{\sqrt{3} \cdot 400 \cdot 0.8} \] #### Step 2: Calculate \( I_{star/delta} \) \[ I_{star/delta} = \frac{I_{DOL}}{3} \] #### Step 3: Calculate Synchronous Speed \( N \) \[ N = \frac{120 \cdot f}{P} = \frac{120 \cdot 50}{4} \] #### Step 4: Calculate Full Load Torque \( T \) \[ T = \frac{P \cdot 60}{2 \pi N} \] Now, I will perform these calculations. Solve the equation by following steps: - step0: Solve for \(N\): \(N=\frac{120\times 50}{4}\) - step1: Reduce the fraction: \(N=1500\) Solve the equation \( I_{DOL} = \frac{15000}{\sqrt{3} \cdot 400 \cdot 0.8} \). Solve the equation by following steps: - step0: Solve for \(I\): \(I=\frac{15000}{\sqrt{3}\times 400\times 0.8}\) - step1: Reduce the fraction: \(I=\frac{375}{8\sqrt{3}}\) - step2: Rearrange the numbers: \(I=\frac{125\sqrt{3}}{8}\) Solve the equation \( I_{star/delta} = \frac{I_{DOL}}{3} = \frac{\frac{125\sqrt{3}}{8}}{3} \). Solve the system of equations by following steps: - step0: Solution: \(\left\{ \begin{array}{l}I=\frac{I}{3}\\\frac{I}{3}=\frac{\frac{125\sqrt{3}}{8}}{3}\end{array}\right.\) - step1: Calculate: \(\left\{ \begin{array}{l}I=0\\I=\frac{125\sqrt{3}}{8}\end{array}\right.\) - step2: Find the intersection: \(I \in \varnothing \) Solve the equation \( T = \frac{15000 \cdot 60}{2 \pi N} = \frac{15000 \cdot 60}{2 \pi \cdot 1500} \). Solve the system of equations by following steps: - step0: Solve using the substitution method: \(\left\{ \begin{array}{l}T=\frac{15000\times 60}{2\pi N}\\\frac{15000\times 60}{2\pi N}=\frac{15000\times 60}{2\pi \times 1500}\end{array}\right.\) - step1: Calculate: \(\left\{ \begin{array}{l}T=\frac{450000}{\pi N}\\\frac{450000}{\pi N}=\frac{300}{\pi }\end{array}\right.\) - step2: Solve the equation: \(\left\{ \begin{array}{l}T=\frac{450000}{\pi N}\\N=1500\end{array}\right.\) - step3: Substitute the value of \(N:\) \(T=\frac{450000}{\pi \times 1500}\) - step4: Simplify: \(T=\frac{300}{\pi }\) - step5: Calculate: \(\left\{ \begin{array}{l}N=1500\\T=\frac{300}{\pi }\end{array}\right.\) - step6: Check the solution: \(\left\{ \begin{array}{l}N=1500\\T=\frac{300}{\pi }\end{array}\right.\) - step7: Rewrite: \(\left(N,T\right) = \left(1500,\frac{300}{\pi }\right)\) ### Results of Calculations 1. **Starting Current with Star/Delta Starter:** - The D.O.L. starting current is given by: \[ I_{DOL} = \frac{125\sqrt{3}}{8} \, \text{A} \] - The starting current for a star/delta starter is: \[ I_{star/delta} = \frac{I_{DOL}}{3} = \frac{125\sqrt{3}}{24} \, \text{A} \] 2. **Full Load Torque:** - The synchronous speed \( N \) is calculated as: \[ N = 1500 \, \text{RPM} \] - The full load torque \( T \) is approximately: \[ T \approx 95.49 \, \text{Nm} \] ### Next Steps Now, we need to calculate the size of switching devices, cables/wires, and protective devices. ### (iii) Size of Switching Devices The size of switching devices can be determined based on the starting current. The rating of the switching device should be higher than the starting current. ### (iv) Size of Cables/Wires The size of cables can be determined based on the full load current. The full load current can be calculated as: \[ I_{FL} = \frac{P}{\sqrt{3} \cdot V \cdot \text{p.f.}} = \frac{15000}{\sqrt{3} \cdot 400 \cdot 0.8} \] ### (v) Size of Protective Devices The size of protective devices can be determined based on the full load current and the starting current. Let's calculate the full load current \( I_{FL} \) and then use it to determine the sizes of switching devices, cables, and protective devices. #### Step 1: Calculate Full Load Current \( I_{FL} \) \[ I_{FL} = \frac{15000}{\sqrt{3} \cdot 400 \cdot 0.8} \] Now, I will perform this calculation. Solve the equation by following steps: - step0: Solve for \(I\): \(I=\frac{15000}{\sqrt{3}\times 400\times 0.8}\) - step1: Reduce the fraction: \(I=\frac{375}{8\sqrt{3}}\) - step2: Rearrange the numbers: \(I=\frac{125\sqrt{3}}{8}\) ### Full Load Current Calculation The full load current (\( I_{FL} \)) is given by: \[ I_{FL} = \frac{125\sqrt{3}}{8} \, \text{A} \] ### Summary of Results 1. **Starting Current with Star/Delta Starter:** \[ I_{star/delta} = \frac{125\sqrt{3}}{24} \, \text{A} \] 2. **Full Load Torque:** \[ T \approx 95.49 \, \text{Nm} \] 3. **Full Load Current:** \[ I_{FL} = \frac{125\sqrt{3}}{8} \, \text{A} \] ### (iii) Size of Switching Devices - The size of the switching device should be rated for at least the starting current \( I_{star/delta} \). ### (iv) Size of Cables/Wires - The size of cables should be rated for at least the full load current \( I_{FL} \). ### (v) Size of Protective Devices - The size of protective devices should be rated for the full load current and should also consider the starting current. ### Conclusion To finalize the sizes of switching devices, cables, and protective devices, you would typically refer to standard electrical engineering tables or guidelines that provide the appropriate ratings based on the calculated currents. If you need specific numerical values for the sizes of switching devices, cables, and protective devices, please provide the relevant standards or guidelines you would like to use for those calculations.

Answered by UpStudy AI and reviewed by a Professional Tutor

error msg
Explain
Simplify this solution

Extra Insights

To answer each part of the question we will provide formulas and some insights into the calculations you'll need to perform. The starting current of a star/delta-connected motor is significantly lower than that of a direct-on-line (D.O.L.) start. Typically, when using a star/delta starter, the starting current can be approximated as \( \frac{1}{3} \) of the D.O.L. starting current. You can calculate the D.O.L. starting current using the formula \( I_{DOL} = \frac{P}{\sqrt{3} \cdot V \cdot p.f} \). Assuming a starting factor of 5, the starting current for the star/delta configuration would be \( I_{start} = \frac{I_{DOL}}{3} \). For full load torque, the rotor experiences a slip of 4%. The full load torque \( T \) can be calculated with the formula \( T = \frac{P \times 60}{2 \pi N_s} \), where \( N_s \) is the synchronous speed given by \( N_s = \frac{120 \times f}{p} \), with \( f \) being frequency and \( p \) being the number of poles. When calculating the sizes for switching devices, cables, and protective devices, considerations revolve around the maximum current ratings, protection against overloads and short circuits, and ensuring that wires are rated for both current capacity and safety compliance. For cables, you can use the current-carrying capacity tables based on the cable material and installation conditions, and for protective devices, select an appropriate circuit breaker or fuse based on overcurrent protection ratings along with the starting current capability.

Related Questions

Latest Engineering Questions

Try Premium now!
Try Premium and ask Thoth AI unlimited math questions now!
Maybe later Go Premium
Study can be a real struggle
Why not UpStudy it?
Select your plan below
Premium

You can enjoy

Start now
  • Step-by-step explanations
  • 24/7 expert live tutors
  • Unlimited number of questions
  • No interruptions
  • Full access to Answer and Solution
  • Full Access to PDF Chat, UpStudy Chat, Browsing Chat
Basic

Totally free but limited

  • Limited Solution
Welcome to UpStudy!
Please sign in to continue the Thoth AI Chat journey
Continue with Email
Or continue with
By clicking “Sign in”, you agree to our Terms of Use & Privacy Policy